  • Sam

    Member
    July 9, 2012 at 4:44 pm

    “This is the same dreaded message you receive while
    driving in extreme heat and the cruisairs will shut down due to the hot
    highway and they usally won’t come back on line until is get cooler.”

    I kept getting the same “HI PS” shutdown on our rear cuiseair unit this past weekend. We were in 105 degree heat, sitting in an open field at a music festival. I tried spraying the ground beneath the bus with water, and that didn’t help. I then tried blowing a large fan under the bus, and that seemed to help some. We just had one shutdown of the rear air unit after that. All was well after the temperature dropped below about 95 degrees in the evenings. But, once the “HI PS” shutdown ocurred, the unit would not run until after several hours of cooling passed. I never could figure out why just the rear unit out of four cruiseairs was affected, however.

  • Larry & Diane

    Member
    July 10, 2012 at 6:32 am

    On hot days I have found it helpfull to raise the bus as high as possible in order to get as much airflow under the bus as possible,you might also check and make sure that the condensor fan on the rear unit does not have any restrictions.I have replaced the condensor fan with a larger fan on one of my units and it was 104 in Lexington,KY on Saturday and that unit preformed the best of all of the 4,it does have a different sound when running but the flow is much greater.I also piched up 2 degrees of differential after the install.

  • Archived

    Member
    July 10, 2012 at 9:37 am

    Like Jack said, raising the coach will help a lot. Liberty’s tend to be a little more sensitive to this when parked. Something else that will help a great deal is running the condenser blower continuously when the A/C is on. This is an easy modification to make, and will help keep the condenser cool. Also some coaches have rubber baffles that extend down below the coach to minimize recirculating hot air. Make sure they are not missing/damaged.

  • Archived

    Member
    July 10, 2012 at 6:25 pm

    Just wanted to add a Hardy THANK YOU to all of the shared input from those who know,for those who did not know, the best ways to keep us all as cool and comfortable as possible while in this heat spell.Thank you all.

  • William

    Member
    July 11, 2012 at 11:03 am

    Now that this thread seems resolved I have another question that is similar but different. If this is the wrong place to post this, please let me know.

    When using the heat pump side of my center Cruisair and the outside temperature starts getting down around 45 degrees F, I often get a “LO/PS” code and the unit shuts down. None of other Cruisair units, which are also in operation at this time does this. What am I being told? (I see from this thread that I am experiencing low suction pressure, but that doesn’t mean much to me). Is serious damage about to occur? What should be done?

    Thanks for any and all help. As Jon says, “whether it is accurate or not”.

  • Michael

    Member
    July 11, 2012 at 12:18 pm

    I would have the refrigerant charge checked. When the units are acting like heat pumps the unit is actually operating backwards with the evaporator functioning as the condenser, in essence transferring heat out into the house instead of transferring it to the outside as it does when functioning as an AC.

    John Klopp……….any advice?

  • Archived

    Member
    July 12, 2012 at 12:06 am

    The low pressure condition is low refrigerant as Jon indicated.

    Unfortunately
    the charging of one of these units on a bus is a series of compromises. The
    original design of the unit intended it to be used as a close coupled system
    meaning the evaporator and condenser were close together. The condenser was
    water cooled producing a condensing temperature that would seldom exceed 100
    degrees F based on a water temperature of around 85 or less.

    In
    order to put the system on a bus the water cooled condenser was replaced by an
    air cooled condenser. This increased the condensing temperature and reduced
    system capacity below the published data for water cooled systems. The condensing
    temperature could be increased to as high as 140 degrees F. Keep in mind that
    the condensing temperature is typically 25 to 30 degrees higher than the ambient
    air temperature entering the condenser.

    With
    R22 refrigerant, having the unit trip on high pressure at 425 PSI represents a
    condensing temperature of 161 degrees F.

    ALL
    compressors and manufactured air cooled units are ARI/ASHRE rated at a
    condensing temperature of 130 degrees F. Any time the condensing temperature is
    higher than 130 degrees F the published cooling capacity of any unit will be
    reduced. Based on an estimated published cooling capacity of 14,000 BTU/hr. I
    would expect the actual cooling capacity to be reduced to about 10,000 BTU/hr.
    capacity when close to trip off on hi pressure.

    The
    critical charge of a system like this is caused by a condenser with insufficient
    capacity for the conditions it is operating in. The condenser has three
    functions. The top rows are used to DE superheat the refrigerant. The
    refrigerant will reach the condenser as a super-heated refrigerant vapor. The
    temperature will often time be 75 degrees hotter than the condensing
    temperature. The superheat is caused by the heat of compression and the cooling
    of the electric motor inside the compressor.

    The
    second stage is where most of the heat transfer takes place due to a change in
    phase of the refrigerant from a vapor to a liquid. The bottom of this area
    represents the condensing temperature.

    The
    third section is sub cooling and is located on the bottom rows of the condenser.
    The sub cooled liquid refrigerant may be sent to a receiver then to the liquid
    line feeding the evaporator. Sub cooling needs to be sufficient to ensure that
    the pressure drop of the refrigerant in the liquid line between the condenser
    and the expansion valve is less than the sub cooling. Any pressure drop or
    increase in refrigerant temperature greater than the sub cooling will cause the
    refrigerant to flash to vapor and deliver liquid with bubbles to the expansion
    valve reducing capacity.

    Imagine
    a condenser 14 rows high, the top 2 are DE superheating, the next 10 are
    condensing and the last 2 are sub cooling. The bottom 2 should be full of
    liquid refrigerant. If the system is undercharged, the bottom 2 will not be
    full of refrigerant and the sub cooling will be reduced causing the liquid to
    flash to a gas prior to reaching the expansion valve. If the system is
    overcharged, the liquid refrigerant will back up into the condenser reducing
    the condensing section to maybe 9 or even 8 rows. The reduction is heat
    transfer will reduce capacity due to a high condensing temperature.

    System
    charging is easy when you are operating within the intended design standards.
    When operating outside of the standard as indicated above, the charge becomes
    critical and compromised. The goal of a properly charged system is to provide
    the maximum amount of cooling without damaging the compressor. As Jon pointed
    out this is generally when the suction line from the evaporator is as cold as
    possible. There must be enough refrigerant in the system to reach the expansion
    valve in a liquid state. The refrigerant is then metered into the evaporator
    were it expands, a phase change takes place and the coils are cooled. If insufficient
    refrigerant is in the system, only a portion of the evaporator will be flooded
    and capacity will be lost. A similar condition will take place if the superheat
    on the expansion valve is set too high. The expansion valve should be set for
    8-10 degrees of superheat. In this case superheat is the temperature rise based
    on the inlet refrigerant temperature and the outlet refrigerant pressure
    measured at the compressor and calculated to be a temperature. The proper
    superheat ensures that all refrigerant has made a phase change and is now a
    vapor at the compressor inlet. A superheat that is too low will allow liquid
    refrigerant back into the suction side of the compressor and destroy the
    compressor in a short period of time.

    And
    now that you understand a basic system, add a reversing valve so you have a
    heat pump. The reversing valve will swap the evaporator and condenser sections
    to provide heat instead of cooling. Anyone see a problem?

    Charging
    to get maximum cooling is a compromise in a bus installation. If you want it to
    work perfectly in a bus installation with heating capability you will have to
    decide if you want to charge for maximum cooling or maximum heat.

    My
    recommendation is to charge for maximum cooling and never use it as a heat pump
    for heat.

    You
    already have several ways to heat the bus without using the heat pump.

  • Ace

    Member
    July 12, 2012 at 6:34 am

    Big thanks John. You are absolutely correct to note since we have multiple heating options in our coaches it makes sense to optimize the AC units for cooling.

  • Ed

    Member
    July 12, 2012 at 8:02 am

    Great explanation John, thanks.

  • Archived

    Member
    July 19, 2012 at 1:03 pm

    John,Do you think that it is a good idea to by-pass (eliminate)the hot gas by-pass valve,and if so should it help performance?

  • Archived

    Member
    July 19, 2012 at 1:42 pm

    Jack,

    In general I
    would not remove the hot gas bypass valve. The function of the valve is to monitor
    the suction pressure/temperature of the evaporator. If the pressure is too low
    the valve opens and hot gas is diverted into the evaporator to keep it from
    freezing or frosting.

    The reason the
    hot gas valve is used is in a low ambient condition the suction pressure will
    drop causing frosting. The evaporator pressure drops in a low ambient condition
    due to an increase in refrigerant mass flow. The mass flow increases due to a
    reduction in condensing pressure allowing the compressor to pump more
    refrigerant.

    If the valve
    is operating correctly and the refrigerant charge is reasonably close, there
    should be no way it will be open during a high ambient maximum cooling capacity
    day.

    If the valve
    has been removed, on a day when the coach interior was hot and the outside air
    was cool, frosting of the evaporator would be likely to accrue.

  • Archived

    Member
    July 19, 2012 at 3:48 pm

    I understand what you are stating,AAP and another cruise air service center tell me that they have had so many failures with the plastic hot gas valve that it is not if but when they will fail so they have begun to eliminate them,I guess that the logic is that it is better not to have it than the problems that could happen without it,I was also told that performance should increase but I have had 2 removed and I did not see any increase in performance.What do you think about increasing the condenser fan capacity and is there any negative to doing it?

  • Archived

    Member
    July 19, 2012 at 9:49 pm

    Thanks for the knowledge and advice. I am convinced. I will have the refrigerant level checked and all of the units maximized for best cooling performance; no more using them for heating.

    Cheers.

  • Archived

    Member
    July 19, 2012 at 11:26 pm

    Jack,

    I would go along with removal if you dont try to run the system below an outside air temperature of 60-65 degrees. No increase in performance will be achived unles the charge was incorrect or the valve had failed.

    You cant have too much air flow or condenser surface. But, if you manage to get a condenser way bigger than the one you have now, you will need to have hot gas bypass.

  • jack

    Member
    July 20, 2012 at 4:55 pm

    Thanks for the response,I have 1 cruise air unit that I have replaced the condensing fan and 2 weeks ago it was 104 in Kentucky and that unit is the only one of 4 that did not have high pressure or thermal shutdown sometime during that heat wave,I have 2 more fans that I am going to install soon.