  • fried inverter

    Posted by Chas on June 26, 2018 at 5:51 pm

    So had a bad storm that fried one of my inverters. Is there a way to isolate it so it’s not allowing power through and allow the generator to feed power to the house directly?

    Jim/Chris replied 8 years, 2 months ago 15 Members · 27 Replies
  • 27 Replies
  • Peter

    Member
    March 20, 2016 at 6:13 pm

    Holy crap! What would cause a DC spike? Just so i know!

  • Will

    Member
    March 20, 2016 at 7:40 pm

    Thought it was yours Tom when I read the thread header.

    Interested in what caused this and if it can be avoided … Other than avoiding running over 33amp on each trace inverter which could burn them out.

  • Davy

    Member
    March 21, 2016 at 5:20 am

    Trying to sort out what happened for sure. Will post once we are able to verify what happened to these units.

  • Jim/Chris

    Member
    March 21, 2016 at 7:06 am

    Joe Carter figured out what happened. He says all electrical wires and components have smoke inside them. I think what happened was the smoke escaped.

  • Archived

    Member
    March 21, 2016 at 8:07 am

    Yep…and once it gets out, you can’t get it back in…

  • Archived

    Member
    March 21, 2016 at 12:05 pm

    all electronic gear runs on compressed smoke. Don’t let the smoke out.

  • Archived

    Member
    March 21, 2016 at 7:01 pm

    Joe Carter must have sat next to Colt most of the seminar.

  • Archived

    Member
    March 21, 2016 at 8:23 pm

    Only part time, Jon double my dues and I had to move so Colt could not get me into any more trouble.

  • Archived

    Member
    June 26, 2018 at 6:44 pm

    Charles,

    I know nothing about a Liberty but when my inverter failed and was sent for repair, I connected the AC power input to the inverter, directly to the AC output from the inverter therefore bypasing the inverter and its transfer switch completely. You have to disconnect them to remove the inverter for repair ( as well as the DC connection from the house batts). By connecting the AC input/output you have the breaker protection still in place and the wire wire should be the same. You will be feeding your inverter circuits just like when you are on shore power.

  • Tim

    Member
    June 26, 2018 at 7:12 pm

    Assume you don’t have an inverter by-pass switch?

  • Chas

    Member
    June 26, 2018 at 7:26 pm

    Bypass switch?where would that be, and can I run the generator with it?

  • Art

    Member
    June 26, 2018 at 7:38 pm

    did you have a surge protector?

  • Ronald

    Member
    June 26, 2018 at 7:41 pm

    I have a nice surge guard that is now dead. Working on getting a progressive ind one to replace it.

  • Archived

    Member
    June 27, 2018 at 8:00 am

    Charles, your vintage Liberty had no provision to bypass a failed inverter. On my 97 I had to create a by-pass so I could still get generator or shore power past the inverters to those circuits on the inverter.

    I do not have the schematics or photos I don’t think but they went with all the documentation and log books when I sold the bus. If you permit me to provide your emial address to the current owner of that bus I will send it to him and ask him if there is a way he could make that information available to you if you want to do an inverter by-pass system. It involved a bunch of rewiring and some switches but when I had the system in place I was able to supply power to important things like the refrigerator and outlets as long as the coach had shore or generator power.

  • Roscoeapproved

    Member
    June 27, 2018 at 5:55 pm

    Made it to ETLC and jeff checked things out, and decided that things looked good. Swapped out the fried inverter, brought it all back up and seems everything is working fine now.

    Couple more things I learned from this.

    On the liberty setup, I could have shut down the inverters, started the generator and been able to run my AC’s rather then sleeping in a sweat box.

    Could have also done what others mentioned and unwired the inverter(s) and wired the power/coach sides together and by-passed the inverter(s). Of course doing all that in a downpour wasnt going to happen. But good to know if I ever find myself in a situation where I need to do it (or build a by-pass setup with a switch like Jon/Tom mentioned).


    Jeff and Lindsay

    91 Marathon XL