voltage imbalance on Powertech 17.5
99 Royale with 1100 gen hours. Most of the time it works fine and shows about 115 volts per leg. Sometimes I can hear an a/c unit laboring to begin a compressor engagement. At the same time I can hear the generator loaded up. When I can get to the meters in time, it invariably shows 1 leg with low volts – maybe 100 volts, and high amps – maybe 30 or 40. The other leg is normal – 115 volts and no amp load. The loaded leg will struggle 5 or 10 seconds and then unload for a while, then try it again, usually the same results. Usually this happens in the middle of the night,so I don’t get to read the meter in time. It seems to have something to do with leg balance, occurring when one leg has no load. It has never happened with both legs loaded, but in the night the units cycle. It has rarely tripped what I assume is the automatic transfer switch – producing a loud slam and all a/c power going off for maybe 10 seconds, then resetting. The engine never dies or struggles, except when heavily loaded as described. It has never done anything like this on shore power, and on gen power it does not seem to happen more when heavily generating. If anything it is the opposite – one leg running an a/c unit and the other leg unloaded. Any ideas? If not, any shop or tech you can recommend? Thanks.