Transfer Switch
Someone please check my logic on this troubleshooting. I went for a warm-up run saturday and when I plugged back into the shore power I had no power on the electrical breaker panel.
I have a contactor based transfer switch made by a now defunct company, no manual, no wiring diagram, no support. Comprised of 2 – 75Amp contactors with a relay to cut the shore power contactor coil voltage if the genny is running. Should the coil fail, the genny power contactor coil voltage is also cut off by a set of aux contracts which are opened when the shore power contactor is closed.
While I suspected the relay, it checks out fine. The auxillary contacts also open and close as they should. So the control system seems to check fine.
I put 120 volts on the shore power contactor coil and it closes as it should. 0.2 ohms across all three poles (2 hot and neutral) power lead contactos when closed and “O.L.” when open.
I put 120 volts on the genny contactor coil and it closes as it should 0.2 ohms across all three poles. BUT BUT BUT when the coil is de-energized and the power contacts are open as indicated by the “manual activation button” I still get 0.2 ohms (indicating a closed switch) across the neutral contactor, 150 ohms across one hot and 200 Mega ohms across the second hot. When I expected to see open circuit indications.
To me this indicated the contactor is bad (I have ordered a replacement). Both contactors are the same model and I would expect the same behavior.
Is there any reason why the neutral should not open? Or all three poles not showing open circuit when the contactor should be open. Is this how contactors fail? I don’t have any experience with these.
Since this is a heavy duty 75 amp switch I prefer to fix it rather than just replace it with a new 50 amp transfer switch.
Confirmation i’m on the right track here?