    Posted by Jim on July 6, 2019 at 2:56 pm

    I previously posted under “wierd electrical” as additional info

    one of the relays in the shore power junction box has a red light. I tried swapping the relay next to it and it “buzzes”

    ** just found out why the buzz-one is 12v the other is 120v( could not see thru the marks a lot)**

    I did check the ac line 1 at the inverter and indeed no voltage, but there is voltage in

    the inverter breaker panel( on all legs) will post pictures of each panel.

    Milo replied 7 years, 1 month ago 6 Members · 5 Replies
  • 5 Replies
  • Roy

    Member
    July 7, 2019 at 11:34 am

    UPDATE!Thanks to suggestion from Ed( Travelingman) I did a “whole coach -shutdown” and it solved the problem. The relay still has a red light ,so will try a new one when it arrives,

    Jim

  • Mark

    Member
    July 12, 2019 at 1:39 am

    Jim,

    This is the fan temp switch at my inverters Coach #632.

  • Deleted User

    Deleted User
    July 12, 2019 at 1:46 am

    Located between inverters. This fan switch controls the temperature that the Marathon installed fans come on to push and pull air out of compartment. I added two more fans to keep inverters cool on hot days or when they are hot. Switch is set as marked in picture.

  • Archived

    Member
    July 12, 2019 at 11:28 am

    Mine is mounted up above the inverters and the snap disc was set a high temp, so for you Marathon guys, check the temp setting and lower it.

  • Milo

    Member
    July 16, 2019 at 7:30 pm

    Update ( again) I replaced the relay that had the red light and new one did not light up. The relay is labeled “inverter loss”

    While I was having trouble understanding why #1 inverter was carrying more load, and for the last couple weeks before they shut down, I was seeing battery voltage drop,

    Now after the reboot, the load is higher on #2 inverter, but batteries remain at 13v &26v.

    Thanks again for the replies.

    Note– wrong picture, this was during “Bulk charge”

    Jim

Log in to reply.