  • SMX Controllers

    Posted by Bryan on January 3, 2014 at 3:21 pm

    One of my SMX controllers has gone bad. Are replacements basically plug and play, or is calibration required? Mine each control on Cruiseair unit for cooling and heat pump and one zone of my Aquahot comfort heating. I think I can figure out programming, but I don’t have gauges and valves if actual calibration is necessary.

    Also, I’m assuming these controllers just get replaced if they go bad, instead of being fixed, but I am not against fixing it if that is possible. Mine does all sorts of weird things, including turning itself on after it has been shut off, failing to properly register indoor temps, and failing to properly take inputs for temperature settings.

    Thanks.

    p.s.: 82 degrees and gorgeous at Outdoor Resorts Indio today!

    Archived replied 12 years, 7 months ago 5 Members · 6 Replies
  • 6 Replies
  • Jim

    Member
    January 3, 2014 at 4:43 pm

    The SMX just plugs in. It talks to the PLM where your programing is.

    Later

    bv

  • Archived

    Member
    January 3, 2014 at 6:48 pm

    Bryan,

    I’ve had some issues with one of mine also, so I unplugged it and then replugged and it kind of rebooted. Give it a try, might work.

  • Roger

    Member
    January 4, 2014 at 5:48 pm

    In addition to trying to “reboot” it as Tom suggested, try switching the suspect control pad with one of the others in the bus and see if the problems stop. I did this on mine several years ago and isolated the problem to the control module box. AAP in Virginia is the source for replacement parts at 804-633-9454. Johnny walked me through the diagnostic process and overnighted the part to me.

  • AL

    Member
    January 7, 2014 at 8:39 pm

    Thanks for great advice. I’ll try moving the controller around this weekend.

  • Archived

    Member
    January 28, 2014 at 8:03 am

    I had the same issue with two of mine, found two loose wires at the control board on one and replaced the control board on the other. The touch pads were both good, I have a spare I use for swapping first.

    There is a system reset that sometimes works for the temp issues. AAP will send you a program card if you do not have one. They are great to deal with and have parts and info.

  • Archived

    Member
    January 28, 2014 at 9:24 pm

    Thanks, Robert. I haven’t got to working on it yet. Good idea about the reset from AAP.