  • Powertech Gen won`t shut down manually

    Posted by steve on December 28, 2014 at 4:00 pm

    17kw powertech starts , picks up load but won`t shut down automatically when battery voltage comes back to preset voltage or shore power restored. Checked 4000 trace inverters to be at factory settings.To stop I pull the throttle linkage back. Any ideas ?

    Reagan replied 11 years, 7 months ago 11 Members · 14 Replies
  • 14 Replies
  • Jerry

    Member
    December 28, 2014 at 4:43 pm

    Can we assume this is when the generator controls are set for auto-start or shore power interruption?

    What does it show as normal operation in the owner’s manual?

    Is your auto start or power interrupt through the inverters and if so what does that say about normal operation?

  • Archived

    Member
    December 28, 2014 at 5:10 pm

    Basic as it gets…. diesel engines stop running when the fuel supply quits.

    Is there some type of control to do what you are doing by hand ?

  • Joe

    Member
    December 28, 2014 at 5:55 pm

    yeap. set to auto start. Gen auto start after battery volts = 22.6 for 30 seconds. This is my choice from inverters setup for normal ops.

  • Chip & Pam

    Member
    December 28, 2014 at 5:57 pm

    only shutdown options are with generator stop button or manually on generator linkage.

  • Archived

    Member
    December 28, 2014 at 6:12 pm

    Does it have a ECU board on the gen in the control box

  • Bryan

    Member
    December 28, 2014 at 7:49 pm

    Steve,

    I would start out by calling Jeff Jones at Powertech. He is the Customer service Tech guy. 352-435-4416

  • Archived

    Member
    December 28, 2014 at 8:35 pm

    Steve, suggest a call to Ben at Parliament. Just had the same problem corrected. Evidently some Vantares were wired incorrectly at the inverters from the get-go. Ours turned out to be a relay and an easy fix. Geo.

  • Sid

    Member
    December 28, 2014 at 9:02 pm

    Believe I`ll give Ben a call. He`s gotten me goin before. Thanks guys ! I`ll report the findings.

  • Tom

    Member
    December 28, 2014 at 9:54 pm

    Steve,

    Since you are able to set the auto start voltage, you may want to think about 24 volts for the start, that’s just under 50% discharge of 24.4, your batteries will last longer.

  • Gary

    Member
    December 29, 2014 at 8:14 pm

    Good thought Tom. I called Dekka last year & talked to their design engineer & he said to “periodically” discharge to @ 50% for battery longevity. He couldn`t define “periodically” so I do it @ every 2-3 months and load up the gen every month.

  • Archived

    Member
    December 29, 2014 at 11:41 pm

    On our 1998 Vantare I had to be sure that the generator was set to the off position on both inverters in order for all the generator functions to work correctly. Just a thought.

    Aren’t you close to Jeff’s place? I bet he knows. Also Ben is a Vantare whiz.

    Good luck.

    Diane

  • Archived

    Member
    December 30, 2014 at 8:35 am

    Steve,

    There’s your problem, you’re using Deka! Just kidding, but when they die, call me for Lifelines..

  • glen

    Member
    January 11, 2015 at 12:15 pm

    Fixed ! For some reason Trace inverter SW4024 menu # 13 for gen starting RY7 function was set to Run instead of Glowstop. This allows a stop signal to shutdown the gen.

  • Reagan

    Member
    January 11, 2015 at 3:10 pm

    That’s what I thought… ours had to be set to stop or off in order to function properly.. if it was on run those functions wouldn’t work on command.

    Glad it’s fixed.

    Diane