  • Odd Voltage Readings

    Posted by granvil on April 12, 2013 at 6:58 am

    Having issues with genset, one leg is showing 135 volts,the other 110( and both vary somewhat) the leg that shows the lower voltage keeps kicking the inverter off when the two a/c’s on that leg are run simultaneously. Just had new batteries installed so could there be a connection?

    Hector replied 13 years ago 10 Members · 15 Replies
  • 15 Replies
  • Gerald

    Member
    April 12, 2013 at 8:03 am

    I’m not a generator expert, but your post suggests you have a problem with the voltage regulator on the generator.

    I don’t know if you can adjust the voltage on each leg or if the problem requires a replacement of the voltage regulator.

    It sounds as though the low output on the one leg drops further when loads are applied so the resultant voltage is below the inverter input requirements.

    Perhaps a Vantate expert can help here, but I presume even though all circuits are run through the inverters that does not mean when an outside 120 volt source is available that the inverters are still inverting. I am guessing the inverters are passing through 120 volt power and using that power input to function as chargers. If the loads are heavy such as the 2 ACs, and the inverters are set for high charging current you could have loads heavy enough to pull the incoming generator voltage below the inverter operating range.

  • Bill

    Member
    April 12, 2013 at 8:09 am

    Jon beat me to it, regulator comes to mind. I’m not familair with Vantare either, but do know everything goes through the inverters. Since the batteries have just been changed, any chance one of the inverters is setup wrong? I’m sure you have Trace and there is a gazillion settings that can be changed.

  • Archived

    Member
    April 12, 2013 at 10:09 am

    Not a generator expert either but it sure looks like you are overloading one side of the split 240V phase when its voltage dips below 110V. Voltage is automatically adjusted via field current and is the same for both sides of the split phase. If one side of the split phase is idle and the other close to max amps, you’d see the voltages your are observing.

    I’d check amps and loads on both sides of the split phase and then try to balance the load better. Put some load on the idle side of the split phase. Highly asymmetric loads are not good for generator longevity.

  • Archived

    Member
    April 12, 2013 at 9:22 pm

    My thought are with Threegreens, I would check the voltage as it leave the generator. If those are different than it’s the generator.

  • JIM

    Member
    April 13, 2013 at 7:06 am

    Thanks for the replies. The voltage leaving the generator and at the inverter is generally the same. When I put a heavier load on the problem leg( inverter 2) then I get a noticeable drop in voltage in that leg as well as a corresponding increase on the other leg e.g. 105v / 135v. If I leave the load on, ultimately the inverter disconnects from the gen and begins inverting and finally over current because of the load I suppose .

  • Archived

    Member
    April 13, 2013 at 7:38 am

    I had my last Trace inverters 7 years ago, but I remember the option in setup for the inverters to supplement power coming from a source, gen or shore, that would boost voltage to prevent brownout. Peak Load or something like that comes to mind. Maybe you can tweak it a little to get you by and add juice to the low voltage leg.

  • Archived

    Member
    April 13, 2013 at 9:47 am

    The inverter disconnects because the voltage drops to 105V (too low). How many amps are you pulling?

    It seems to me that the voltage regulator in the generator is trying hard to raise the output voltage. That is why the other leg is at 135V. The low leg is either overloaded pulling the voltage down or there is a partial short in the generator windings of that leg. How is the voltage when the generator has no load applies? Is it the same for both legs?

    Do the inverters work fine on shore power? Same loads?

    Gerald

  • Archived

    Member
    April 13, 2013 at 10:42 am

    I think Gerald has the question that goes to the heart of the problem.

    Good one Gerald!

  • David

    Member
    April 13, 2013 at 10:56 am

    I’m in the camp that says it’s the generator, likely the regulator. When one leg drops in voltage the other should not rise. In fact, at 135V that leg’s voltage is too high. One interesting note is that your generator is maintaing 250V between leg 1 and 2.

  • Peter

    Member
    April 29, 2013 at 6:28 pm

    So, at this point I’m being told it is a bad fuel pump, wouldn’t allow genset to make sufficient RPM./ Power

  • Archived

    Member
    April 29, 2013 at 8:27 pm

    How are they explaining the voltage? I hope the injection pump works although I’m doubtful.

  • Archived

    Member
    April 30, 2013 at 5:33 am

    I just got the message, I will ask , but I too wonder how it would only affect one leg. The only explanation is that leg had a heavier load and therefore was being impacted more.

  • Rod

    Member
    September 7, 2013 at 2:46 pm

    Did this ever get corrected?

    Gil’s comment about the voltage adding to 250 volts got me thinking.

    Bad/loose neutral or ground?

    Ed Roelle

    98 Royale

  • Hector

    Member
    September 19, 2013 at 8:36 pm

    When you have such mismatched voltages, it is due to either no or poor neutral wire and terrible miss matched loading on one leg.

    Both issues are non exintant when wired as 120 volt only. When using the 120/240 volt connections is when load balancing is important and required for a nice running system. Some of the things that occur with such high voltage, you start to burn up things.. UL Listed equipment spec is 10%+/- voltage and 5% +/- frequency.

    Cheers

    Dave M

  • Jerry

    Member
    September 19, 2013 at 9:25 pm

    I’m really involved in generator repairs right now. And on mine, the
    power to the Generator breaker has a jumper that connects both legs
    feeding the breaker. On the output side of the breaker, they are
    separate going to the Inverters.

    If yours has the old brown
    plastic box with a bunch of white wires for a regulator, I would look
    there first as most have suggested. I had some simular erratic voltage
    readings out of mine, but they were from 119v all the way down to 15.4v.

    If you change regulators, the new style will be analog, and make sure you talk to someone before wiring up the new regulator, I’m assuming you have a Powertech. If so, call Jeff Jones there, he can direct you. It does not wire up anything like the one that’s in it. (if it’s the brown plastic one)

    Also, there are manuals on their website that will give you a sequence of steps to check.