My annual DIY CruiseAir TuneUps
Tuned up the 3 CruiseAirs today. 85F humid day. R22 30 Lb tank static pressure 160 psi. Exactly as it should be under these conditions.
To access the aft condenser king valves had to drain and remove fresh water tank.
Aft unit initial static pressure 120 psi. Its low on freon. Initial gauge pressures before adding freon 53/185 psi and king valve temps before adding 82*/88*. Added R22 a little at a time until pressures were 68/255 psi and king valve temps were 41*/107* and air duct outlet temp of 50* w/temp gun and 55* on analog thermometer, and inlet air duct temp of 81*.
Lowered front bumper.
Mid unit initial static pressure 150 psi. Probably doesn’t need any freon. Gauge pressures were 72/260 psi and king valve temps were 49*/100* and air duct outlet temp of 49* w/temp gun and 55* on analog thermometer, and inlet air duct temp of 83*. Didn’t need to add freon.
Fwd unit initial static pressure 145 psi. A little low on freon. Initial guage pressures before adding freon 65/255 psi and king valve temps before adding 64*/112*. Added a little R22 until pressures were 70/270 psi and king valve temps were 65*/120* and air duct outlet temp of 49* w/temp gun and 55* on analog thermometer, and inlet air duct temp of 84*.
In the end all three units had condensation coming from their drain at a rate of about 1 drop/sec. SWEET!