  • Kohler Generator – Fault Code

    Posted by Loc on November 11, 2019 at 12:55 pm

    I have had this happen twice – both times starting the generator in 30 degree or colder weather when the generator is cold. It will start and run for approximately 2 minutes and then shut down and throw a OU – over volt code. I have tried resetting the ECU and re-starting the generator which will re-start but shuts down within 20 seconds and throws the code again. Any thoughts?

    Other than these two times, the generator has performed as intended.

    It is a 20KW Kohler generator in a 2008 Marathon.

    I realize the short between the driver’s seat and the start button is likely a contributing factor.

    Archived replied 6 years, 1 month ago 6 Members · 6 Replies
  • 6 Replies
  • Bob

    Member
    November 11, 2019 at 1:34 pm

    First item to check …all the connections inside the generator mounted black control box.

    Push in connectors and crimped wire connections have a history on generators due to continuous vibration.

    AL

  • DON

    Member
    November 11, 2019 at 3:41 pm

    Will do Al. Thanks.

  • Archived

    Member
    November 11, 2019 at 4:07 pm

    This is just a wag, but I have had to replace two voltage regulators on my Kohler, one failed allowing over-voltage and one was erratic, shutting the gen down at random times due to low voltage.

  • Bill

    Member
    November 11, 2019 at 5:05 pm

    Loc, have you tried starting from the gen with remote switch off? Also, assume auto start is off.

  • Harry

    Member
    November 12, 2019 at 6:47 am

    Have not Tom but I will try that. Thanks

  • Archived

    Member
    July 30, 2020 at 1:13 pm

    Does the vr come pre set or must it be adjusted ?