INVERTER SHUTDOWN
During the recent Polar Vortex (Tks Al Gore !!) temps dropped to -3 deg F here in Knoxville,TN. This caused utility votages to drop to 103 & 106VAC on my shore power causing my #2 Inverter to shutdown due to the 24VDC / 250Amp circuit breaker(see pic) trip which dropped loads on the right side of the inside load panel (see pic). The loads were picked up by house batteries & then when battery voltage dropped to the setpoint the Genset fired up.
To prevent a reaccuring issue , Inverters` incoming voltage set point was changed from 108 to 105VDC and all has been well. Big thanks to Ben Cummings at Parlimant Coach for the assisting phone call to discover the tripped breaker. Hope this helps someone.