Help – Transfer Switch issue ?
Hello all,
On every coach I have had, when the shore cord is connected, you hear a clunk as the transfer switch engages and powers the bus.
I can not hear a thing on this Vantare. I need to check connections inside that switch when I find it to figure out why the shore power from a 20 amp source does not latch the inverters relays onto charging…..
Here is what it does….on Generator I get 115-119 V for each leg and everything seems fine.
When I was on 50 amp shore power it was reading 115-120V incoming on each leg and all was good.
Now on a 20 amp breaker with adapters, I check the voltage on the cord end before I plug the bus in and get 118V but when the bus is connected…first, I don’t hear the thump that power has been applied, second, the “AC2 Good” green LEDs blink and the inverters would not latch onto the source and when I check incoming volts readout on the Inverter panel I see 98-100V…..What the heck ?
I go back out, voltmeter on the cord before connecting the shore, I get 115V, connect it back, same blinking on the remote panel and 15 Volts lower….
Now…according to the manuals, shore power should be wired on “AC1” input and “AC2” is Generator. When I was on 50 amp shore the AC1 led was lit and latched. When the generator runs the AC2 is lit and latched. When i am connected to shore through 50 amp to 30 and 20 amp adapters, I would believe that I should still see the power coming in on AC1 but no….it blinks the AC2 input……something is not right ?
So…..any ideas ? Where is the transfer switch on a 98 Vantare ?
I found the 2 manual power switches that isolate/bypass the Trace 4024 inverters and when I flip them to Utility I don’t get power to the breakers on both legs and with inverters out of the loop….. That tells me that I could have a transfer switch problem and the shore power is not coming through…..is my thinking right ?
I tried different 50/30/20 amp adapters, also got two different 20 amp circuits and fed the bus with 2 cords and a “Y” adapter delivering independent 20 amps to each leg…same problem, same 15-18V drop on both legs on inverter remote panel once it enters the bus.
What do I do ? I need to figure this out asap to be able to plug it in and charge the batteries…..
Thank you for any advice.