Failed 4024 Inverter and fix
Last week I went out to the bus and found that one of my 4024 inverters had shut down. I had replaced a 300 amp T type fuse last year to fixed the same problem so that is the first place I looked. I measured the voltage at both ends of the fuse and had 28 Volts at the battery end and 6.4 volts at the inverter end. I did not think much of it since that was the same reading I had with last year’s failure and an electrian friend told me these fuses were encased in a sand like material and could leave a carbon trail that could conduct a smal amount of current.
After replacing the fuse I had the same readings so that concerned me. I removed the cable from the inverter and then that end of the cable begin reading 21 volts. While removing the fuse to check and tighten all the wiring connections I had that small spark again and I noticed that the square block on the Xantrex fuse holder that the fuse uses as it’s contact moved. When I checked further it would spin on the bolts that holds the fuse. Using a pair of pliers I tighened both of the blocks and all wires connections and replaced the fuse and the cable to the inverter and all worked great. I now suspect that may have been my issue last year and the fuse I replaced was not bad either. Just one more thing to check when working on these units.