  • Dometic control did not control HVAC

    Posted by George on October 21, 2022 at 9:32 pm

    Strange events

    no function on dometic control would function

    Reset dometic by holding top and bottom buttons turn on the on off switch

    display showed FF

    the fan and heat pump started to work but the AC units were blowing cold air not heat

    Furnace would not bring on any of the three zones

    Removed aquahot cover and can bring on all three zones y shorting to ground

    question why control will not start zones

    Roscoeapproved replied 3 years, 11 months ago 3 Members · 2 Replies
  • 2 Replies
  • Dave

    Member
    October 22, 2022 at 9:47 am

    On my coleman you can only go 4 degrees at a time. If you try to go more than the 4 degrees it tries to turn on the gas heat. I don’t have gas heat so when it is cold I just move the setting by the 4 degrees.

  • Roscoeapproved

    Member
    October 22, 2022 at 9:58 am

    Check underneath wiring, When they removed your AC’s maybe they forgot to connect the Blue wire,That sends 12v to heat be it a furnace or Aqua Hot, It send 12v to heat source,a furnace it activates it on a older Aqua Hot the 12v goes to 3 cube relays that changes a 12v signal to a negative signal. After 2003 newer Aqua Hot units with control boards the 12v signal turns it on. You have a cube relay for each zone Bedroom/Bathroom/living room. Here is a Royale wiring schematic for your model and year. See 4 cube relays extra one for Bay Heat, Those cubes are right near Aqua Hot same compartment


    Jeff and Lindsay

    91 Marathon XL