DIY Cruisair Service
Its still warm here in TX so I decided to checkout all 3 Cruisairs this morning.
The aft unit was barely cooling at all. The fwd unit was ok but not cooling as well as the mid/portside unit. All condensors, evaporators, and filters are clean. All units are controlled by SMX II units.
I have a big 30 Lb bottle of R-22. My ac gauges/hoses are for R-12 w/removeable R134 adapters. For your info, R-22 system fittings are the same as R-12. When it comes to pressures, I’m happy using the outer scale on my gauges. For evaporator exh air temps I have several cheap small temp gauges made specifically for ac work(not pictured). I use the cheap CenTech(Harbor Freight) IR temp gun to obtain quik accurate suction line temps where the suction hose hooks onto the king valve. The King valves have plastic o-ring sealed caps(13/16″) are opened by turning the valve stem clockwise(inward) 1 full turn using 1/4″ wrench or 12 pt socket.
It was a humid 72f inside and outside the coach this morning. My goal was to get the fwd & aft units blowing 42f air like the mid/portside unit. I was able to do this by adding R-22 until the suction temp lines on the aft & fwd units matched that of the mid/portside unit, 42f. All three units eventually cycled on and off and were blowing 42f air. Pressures ended up being 70psi and 210psi.
I hope this helps.