    July 22, 2012 at 12:16 pm

    I’m
    going to disagree with replacing the compressor prior to checking the overload.

    The overload is a Klixon thermo disk that is connected to the compressor common
    terminal with a spade clip. The start and run terminals are also connected with
    spade terminals. The fact that the wire to the overload is burnt suggests that
    the common spade clip to the overload was loose. This type of failure is common
    and there is a kit available from most parts houses that will replace the spade
    clip with a screw on clip if the compressor terminal has been damaged. You
    should be able to get a new overload and a spade terminal screw on kit for
    around 30 bucks.

  • Ken

    Member
    July 22, 2012 at 6:53 pm

    Thanks John, I have ordered the overload from AAP and will check those connections also. Since this is the easy and least expensive way it is worth a try.

    Bill

  • Ronald

    Member
    July 28, 2012 at 2:58 pm

    Taking your advice,John, I replaced the thermal overload, cleaned all connections and it seems to have solved the problem. I have run it for about 4 days and nights in my barn so maybe I got lucky.

    Bill

  • Dan

    Member
    July 29, 2012 at 4:32 pm

    That is great,I would have bet that the compressor was done.