Cruisair Parts
Posted by Richard on April 7, 2014 at 3:13 pmI am in need of a cruisair blower motor in my condensing unit behind the bumper, can someone give me a source for the part please? A bearing has gone south and I can’t run the unit until it’s replaced.
I am also going to have to remove and replace both condensors for the job, one is in front of the other (:-( I have been looking for the system specs for pressures, but can’t locate any, does anyone by chance have them?
I am planning on recovery and vacuuming the system, I just need to know I am back to normal range when complete.
Richard
Bill replied 11 years, 4 months ago 7 Members · 9 Replies -
Richard,
I would be very surprised if you could not match your condenser motor with a new one from WW Grainger. Just make sure the problem is the motor and not a start or run capacitor if so equipped.
The system pressures are whatever the refrigeration charts spell out for R-22 and are based on temperatures. As a guide we have learned from others the best performance is usually when the temperature at the suction line is at its coldest. A good rule of thumb is if the sight glass is showing a liquid with ample bubbles it is just about right. All liquid or a visisble foam tend to be too much R-22 or too little. The units are very sensitive to the right charge.
Thank you, I will look it up when I get it out and see if grainger carries it.
Richard -
If you still need the specs, contact me. joelselman@selmanrealestate.com
2005 XL Thompson Coach
Hi All!
Just a quick follow up post.
I need to replace the same motor; but I’d like to have it on hand before I remove the cruisair.
My hope is that I can have an HVAC technician there to empty and refill the unit.
The technician can check/top off the freon in the other 3 units while I swap the motor.
Would anyone happen to have the specs/Grainger part number for the motor that powers the squirrel cage?
Thanks in advance!
Hi All, I just finished repairing 2 of my cruisair units.
The first required a new condenser fan motor. Called Grainger and tech matched it up. Grainger # 5WJC4.
The replacement was a double shaft motor. Just hacksaw off the extra shaft, noting correct rotation. Check twice, cut once. about $1600 Wired up, ran fine, topped off R22 charge. Achieved 10 degrees superheat, and about 9 degrees subcooling. Suction line at condenser unit was 40 degrees. Very pleased with efforts.
The other unit required a new compressor. Searched and found one from Controls Central. centralcontrols.com
unit number Tecumseh AKA5512EXA (AK111AT-004-J7) 120 volt R22 1 hp 12000btu. $3370, plus 32 shipping. It was an identical unit, and required minimal plumbing rerouting. The compressor had been replaced before, and I did not like the tubing routing, and made some changes. Also replaced the capacitors. Grainger 2MEC9 for the run capacitor, and 6FLUS for the start. Ordered a new filter drier, but did not receive a suitable replacement, so skipped it. Left the vacuum pump all night, to maximize moisture removal. Hope it doesn’t come back to haunt me.
Curre
ntly runs fine. Similar performance numbers to the other unit.
Hope this answers some questions for other members.
Dick
Good post Dick. A lot of condensing units just need repair and your post will help others understand those repairs are much less expensive than replacement.
Dick,
I just ordered one for pickup @ Grainger.
Thanks a million
I know that the Tecumseh AK111AT-004 will work as a compressor but it is only rated at 12,000 BTU where the origional cruise air compressor is rated at 15,000 BTU and it is #AK147AT-009.The cruise air condensing unit is rated at 14,000 BTU and I assume that the smaller compressor will work but I would assume that it would not cool as well as the correct one.I know that the cruise air compressor can only be sold by their distributors and is expensive(around $700) but if the smaller one works and cools well then it is a bargain.