This equipment the min splits are engineered and quite a bit different then your original cruise air units. For one the mini splits uses the referagerant lines as the expansion device. If you are going to make a change from r22 to r410 then you must flush the referagerant lines with the proper flush kit as the oils are not compatable and will take out the compressor over a couple of years. If you want to use the existing air handlers for heat and the condenser matches you would need to add the appropriate metering device ( expansion valve) that is rated for the proper size and refrigerant. To replace the coils you would need to know the size tubing, area and fins per inch and make a match accordingly. To small and system will go off on high pressure in heat, to large and the cooling pressure and temperatures will not be correct. The control systems in the mini split world also work much different. On a better note some of the mini split manufactures today are making small air handlers to match the condensers which may be a better alternative based on your particular needs. Hope this helps.