  • Breaker trip

    Posted by Peter on April 5, 2013 at 5:15 am

    I just got to a place and went to plug in kept blowing breaker have being here before lots could not see why battery was on float charge inverters set at 5amps each power was 30 amp so I started to look at problem it turns out the breaker at panel had GFI breaker u can not have two GFI’S bus has one too changed breaker at panel with no GFI problem fixed just food for thought Just put 2300 miles on this week everything worked good bus and house Start clinic to day 200 people here. To see me will be good 4days Film crew here will be with me for couple weeks

    glen replied 13 years, 6 months ago 3 Members · 3 Replies
  • 3 Replies
  • glen

    Member
    April 5, 2013 at 6:47 am

    If you are saying you attempted to use 2 30A GFCI outlets to power your coach, then you shouldn’t be surprised that the GFCI breakers tripped. The coach’s common neutral is the reason why. There’s nothing wrong with the coach or commercial power. Again, I’m assuming you were trying to power the coach from two 110V GFCI protected outlets.

  • Archived

    Member
    April 5, 2013 at 7:46 am

    Post some pictures of the Clinic Peter.

  • Archived

    Member
    April 5, 2013 at 11:10 am

    it is one 30 amp plug 110 there is not two here