  • Air Conditioning Temp Spread

    Posted by Archived on February 21, 2012 at 6:48 pm

    I have the Duo Therm Comfort Control single thermostat that controls the Aqua-Hot, Heat Pumps and A/C. The front of the bus temperature is controlled at the thermostat, the galley and bedroom temperature is controlled by remote sensors that look like this:

    My problem is there is a very large temperature spread between the actual interior temperatures and the thermostat settings. Somtimes the spread is 4 to 6 degree’s and other times it’s closer. There is no method to adjust the temperature spread at the thermostat and is it possible these temperature sensors go bad?

    Rick & Denise replied 14 years, 5 months ago 6 Members · 15 Replies
  • 15 Replies
  • Archived

    Member
    February 24, 2012 at 7:31 am

    Bump….. Where are all the HVAC experts?

  • Archived

    Member
    February 24, 2012 at 12:42 pm

    Ahhhh , Truk, its winter for a lot of us “Unfortunates” not currently in the warmer climes….soon though, and I will be looking for a Cruise AC maintenance somewhere between Arkansas and Alabama…any thoughts all?

  • Archived

    Member
    February 24, 2012 at 5:35 pm

    Winter, it was 84 here today, but I soon need to head home and it will probably be in the 60’s in GA.

    Suggest you call AAP and ask about service in the states you will be heading to.

    http://www.aap.com

  • Roger

    Member
    February 25, 2012 at 6:09 am

    Yom who is AAP?

  • Archived

    Member
    February 25, 2012 at 7:40 am

    Gary,

    They are the Cruisair folks in VA.

  • Archived

    Member
    February 25, 2012 at 9:15 am

    I saw the picture above couple of days ago. I thought it was a floor drain !

    Always here to help

    AL

  • Archived

    Member
    February 25, 2012 at 9:55 am

    Thank you Al for helping! It’s a Hockey Mask….

  • Rick & Denise

    Member
    April 16, 2012 at 9:02 pm

    Tom,

    There are two basic types of sensors. One is a thermistor and can not be calibrated unless the logic is built into the controller. Lower cost controllers seldom have this function. The second type is an RTD that changes resistance with temperature. Calibration is by adding a resistor in series or parralel to change the resistance seen by the controller.

    Controllers in this price range are seldom accurat. What you should consider is rapetability. Does each zone temperature repeate it’s display temperature as the temp changes then returns regardless of the difference with other zones?

    If it does just accept that the difference between the zones will always be a little off.

  • Wayne

    Member
    April 17, 2012 at 6:35 am

    Thanks for the explanation John. I
    suspect the problem is the boards as they are not consistent. As an
    example, the bedroom unit is the worst offender, I may have to push
    the thermostat up or down as much as 6 degree’s or more to achieve
    a start or to shut down. There doesn’t seem to be any consistency.

  • Jim/Chris

    Member
    April 17, 2012 at 7:18 am

    Just call it a comfort control. Scratch out the degree marks and set them to what you feel is right.

    JIM

  • Archived

    Member
    April 17, 2012 at 10:11 am

    That would work Jim, but I have the single thermostat that controls all three units, A/C, Heat Pumps, Aqua-Hot and it’s digital.

  • Archived

    Member
    April 17, 2012 at 4:14 pm

    Tom, mine is the same way. The bedroom is about 6 degrees high, so I have to set the thermostats for that zone 6 degrees lower than the other two.

  • Archived

    Member
    April 17, 2012 at 5:29 pm

    That’s pretty much what I do also Charles.

  • Archived

    Member
    April 18, 2012 at 3:18 pm

    Tom,

    The boards provide a mounting point for the sensors and a termination point for the wires. Recomend you record the temperature diffrences then swap the boards around and compare data. I suspect the diffrences recorded before the move will be transferd to the new location. If that is the case, you have conformed the diffrences are located on the remote sensor boards and not on the controler that is sampling data from the 3 remote zones.

  • Bob

    Member
    April 18, 2012 at 7:43 pm

    Thanks John, that will be my next
    project and I’ll probably be back to you seeking more advise. This
    HVAC stuff is a little frustrating, mainly because I don’t completely
    understand the logic and how all the assorted components for A/C
    come together.