20 KW Kohler – Voltage
Posted by Archived on March 8, 2013 at 6:58 pmAnyone know if the voltage is adjustable on the 20 KW Kohler? Mine when loaded up with 30 – 40 amps on each leg will get down in the 112 volt range and when unloaded, around 116/117.
I had a Powertech and the voltage regulator was adjustable, but can’t find any info on this one.
Archived replied 13 years, 6 months ago 3 Members · 9 Replies -
9 Replies
-
Don’t take this to the bank but there are some causes and some adjustments I think.
The generator should have voltage adjustment potentiometers and the manual should show how to adjust them. I think engine speed has to be correct also, but I believe that controls frequency more than voltage.
Do you have the Kohler manuals? Are they on line?
-
I am not by the bus right now, but I had to play with the engine speed to get the freq. right on mine. It was at about 62 hz. and it screwed up all the clocks. I got it back to almost 60, but it is finicky. I can look through my books when I get home, but I don’t recall a way to change the voltage.
I wonder if that is in the ADC control that is password locked? Tom..how about a call to Liberty?
-
I have the manual, but no joy on any adjustment instruction or information. Not sure if it’s turning at the correct rpm’s, but it does not flucuate when I load it up and stay’s steady.
-
This is the Kohler service manual 20 KVA as used on a 1997 LIBERTY.
If I can not upload it I will send it to Tom and he will.
JIM
-
I had to replace the voltage regulator on mine due to erratic performance causing gen shutdown; I don’t recall any adjustment provided. If you still need info, I can go to the coach tomorrow for the manual. Are you sure you have a problem? What are the normal voltage ranges?
-
Not sure Joel, but like I said, when loaded up with 30 – 40 amps on each leg it will get down in the 112 volt range and when unloaded, around 116/117.
Seems like it should be 120 like the others that I have had. I have the owners manual, but not the service manual. Don’t go to any trouble for the manual, not sure I could do anything with it without special tools. 112 volts is too low in my opinion.
Jim – Send me the internet link for the PDF you sent me, I can’t load the PDF on the site. Mine is a model 20EOR and not covered on what you sent me.
-
That is all I have Tom,I got that about four years ago from the Kohler service center tech. in Cloumbus, Ohio.
JIM
-
Tom.
If my brain and post-its don’t fail me I will bring a copy of a pertinent part of the Kohler manual that might help to Oysterfest.